finding the plcnext through wifi ?
Hi everyone , iwas able to find the plcnext through the ethernet wire connection, but i can't find the plcnext throughWi-Fi, (yes i turn on either the Wi-Fi or lan one at time), any suggestionsor settings that i should add .
Im using laptop with windows10 and plcnext 2021.6 firmware
Im using laptop with windows10 and plcnext 2021.6 firmware
Comments
1. find the PLC in the Search window in PLCnext Engineer?
2. Connect to the PLC from PLCnext Engineer?
3. Open an SSH connection to the PLC from a Windows command prompt?
For (1), please check:
- the correct adapter is selected in the drop-down list in the Project -> Online Controllers window.
- the WiFi device is a Layer 2 device. The DCP protocol used to discover PLCnext Control devices is a layer 2 protocol, so cannot be routed.
- If these don't work, you could try assigning the required IP address to the PLC using the direct cable connection, and then switch to WiFi for programming.
For (2), please check:
- the correct adapter is selected in the drop-down list in the Project -> Online Controllers window.
- The IP address of the PC's WiFi adapter is in the same subnet as the PLC.
For (3), please check:
- The IP address of the PC's WiFi adapter is in the same subnet as the PLC.