The PN device cannot be scanned by PLCnext Engineer

edited September 2021 in PLCnext Engineer
The Siemens D410-2 DP/PN Controller cannot be scanned by PLCnext Engineer(2021.6.1 Build 4.10.294.0 or 2021.0.2 Build 4.7.1183.0). However the PN device can be found both in Netnames+ or PC WORX(6.30.2519). The controller is used to control the Weiss rotary table(TC0220T). Is there any solutions to solve this problem?

Comments

  • Hi kkzahng,

    this might be caused from a known issue with npcap, please find below a statement from the PLCnext Engineer change notes (available in the download center).
    If the online-device editor is not able to find any controller or PROFINET device, it might be caused by a corrupt npcap installation. In this case, proceed as follows:
    – Check the status by entering the following command in the command line shell: „sc query npcap“
    – If anything other than “4 RUNNING“ is displayed in
    the line “STATE“, the configuration has to be
    changed.
    – To do this, enter the command
    “sc config npcap start=auto“ followed by the command “sc start npcap“.
    If there are still no online devices found, Npcap has to
    be reinstalled. To do this, proceed as follows:
    – Uninstall PLCnext Engineer.
    – Uninstall the Npcap software.
    – Install PLCnext Engineer again.

    Have agreat weekend,
    Frank
  • Hi Mr. Frank,
    Thanks for your response.
    As you see in the first attachment, The PLCnext engineer could scan PN devices except this Siemens controller. The npcap function looks like working normally.
    However, I also took the steps that reinstalled the npcap. The device still not on the list of PLCnext engineer--profinet-- "Online devices".
    Have a nice day! Looking forward to your reply.
  • The issue were caused on a bad return of the PN device.
    With the PN DCP answer of the device is also a role definition included.
    The PN scan in PLCnext Engineer filters at this stage for the role "IO-Device".
    In this case does the PN Device answer only with the role "IO-Controller", so the "IO-Device" role were missing and the device is therefore not shown in PLCnext Engineer.