The PN device cannot be scanned by PLCnext Engineer
The Siemens D410-2 DP/PN Controller cannot be scanned by PLCnext Engineer(2021.6.1 Build 4.10.294.0 or 2021.0.2 Build 4.7.1183.0). However the PN device can be found both in Netnames+ or PC WORX(6.30.2519). The controller is used to control the Weiss rotary table(TC0220T). Is there any solutions to solve this problem?
Comments
this might be caused from a known issue with npcap, please find below a statement from the PLCnext Engineer change notes (available in the download center).
Have agreat weekend,
Frank
Thanks for your response.
As you see in the first attachment, The PLCnext engineer could scan PN devices except this Siemens controller. The npcap function looks like working normally.
However, I also took the steps that reinstalled the npcap. The device still not on the list of PLCnext engineer--profinet-- "Online devices".
Have a nice day! Looking forward to your reply.
With the PN DCP answer of the device is also a role definition included.
The PN scan in PLCnext Engineer filters at this stage for the role "IO-Device".
In this case does the PN Device answer only with the role "IO-Controller", so the "IO-Device" role were missing and the device is therefore not shown in PLCnext Engineer.