Hello, my name is Iván!
We ran into with this error (ACT BUS FAIL (0x00c4), ErrorCode=0x0c01, AddInfo=0x0001) in our [b]AXC-F 1152[/b] Cockpit - Notifications table , we changed Axionlane F backplane and AXL F BS BK, but this error is still appearing.
In the backplane are connected AI, DI and DO. When the error appears the values of this intputs came to zero.
In attached files you can find the plc logs and also a picture where a temperature variable is represented to show the problem.
Should we update the PLC firmware from HW: 04 FW: 2021.6.0 to HW: 04 FW: 2021.9.0?
Thank you so much in advance
[code type="markup"]
18.10.21 11:18:03.353 Arp.Services.ProfiCloudV3.Internal.Algorithm ERROR - Hash can not be calculated of non existing file.
18.10.21 11:18:03.354 Arp.Services.ProfiCloudV3.Internal.Config.ConfigurationManager WARN - The hash of the tsd metrics config file could not be calculated.
18.10.21 11:18:03.354 Arp.Services.Ehmi.EhmiComponent INFO - 2661331648 OnPlcChanged success=true, dcgFullReload=false
18.10.21 11:18:03.656 Arp.Services.DataLogger.Internal.Session WARN - Session 'Datos_horas_funcionamiento' (foreground): Adding variable Arp.Plc.Eclr/ALI_HMI_iR_H_RESTANTES_MNTO_B_PURIN to returned: NoSuchVariable
18.10.21 12:24:35.058 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Application Device Address for slot 7 with error code 3858
18.10.21 12:24:35.059 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Failed to read Axioline module info data for slot 7
18.10.21 12:24:35.064 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Vendor Name for slot 8 with error code 3859
18.10.21 12:24:35.065 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Object Location for slot 8 with error code 3859
18.10.21 12:24:35.066 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Equipment Identifier for slot 8 with error code 3859
18.10.21 12:24:35.067 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Application Device Address for slot 8 with error code 3859
18.10.21 12:24:35.067 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Failed to read Axioline module info data for slot 8
18.10.21 12:24:35.071 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Vendor Name for slot 9 with error code 3859
18.10.21 12:24:35.071 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Object Location for slot 9 with error code 3859
18.10.21 12:24:35.072 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Equipment Identifier for slot 9 with error code 3859
18.10.21 12:24:35.072 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Application Device Address for slot 9 with error code 3859
18.10.21 12:24:35.072 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Failed to read Axioline module info data for slot 9
18.10.21 12:24:35.077 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Vendor Name for slot 10 with error code 3859
18.10.21 12:24:35.077 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Object Location for slot 10 with error code 3859
18.10.21 12:24:35.077 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Equipment Identifier for slot 10 with error code 3859
18.10.21 12:24:35.077 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Application Device Address for slot 10 with error code 3859
18.10.21 12:24:35.078 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Failed to read Axioline module info data for slot 10
18.10.21 12:28:54.466 CommonRemoting INFO - Connection was lost remotely, connectionId=AFA66963
18.10.21 12:28:54.468 Arp.System.UmRscAuthorizator.Internal.UmAuthorizator INFO - Clearing authentication: securityToken=BE860E52
18.10.21 12:28:54.468 CommonRemoting WARN - Remoting endpoint of session 'AFA66963' was closed yet, which might indicate a remoting error
18.10.21 12:32:34.558 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Vendor Name for slot 1 with error code 3858
18.10.21 12:32:34.559 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Object Location for slot 1 with error code 3858
18.10.21 12:32:34.559 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Equipment Identifier for slot 1 with error code 3858
18.10.21 12:32:34.559 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Application Device Address for slot 1 with error code 3858
18.10.21 12:32:34.559 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Failed to read Axioline module info data for slot 1
18.10.21 12:32:34.565 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Vendor Name for slot 2 with error code 3859
18.10.21 12:32:34.566 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Object Location for slot 2 with error code 3859
18.10.21 12:32:34.566 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Equipment Identifier for slot 2 with error code 3859
18.10.21 12:32:34.566 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Application Device Address for slot 2 with error code 3859
18.10.21 12:32:34.567 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Failed to read Axioline module info data for slot 2
18.10.21 12:32:34.573 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Vendor Name for slot 3 with error code 3859
18.10.21 12:32:34.574 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Object Location for slot 3 with error code 3859
18.10.21 12:32:34.574 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Equipment Identifier for slot 3 with error code 3859
18.10.21 12:32:34.575 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Application Device Address for slot 3 with error code 3859
18.10.21 12:32:34.575 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Failed to read Axioline module info data for slot 3
18.10.21 12:32:34.580 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Vendor Name for slot 4 with error code 3859
18.10.21 12:32:34.580 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Object Location for slot 4 with error code 3859
18.10.21 12:32:34.580 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Equipment Identifier for slot 4 with error code 3859
18.10.21 12:32:34.580 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Application Device Address for slot 4 with error code 3859
18.10.21 12:32:34.580 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Failed to read Axioline module info data for slot 4
18.10.21 12:32:34.585 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Vendor Name for slot 5 with error code 3859
18.10.21 12:32:34.586 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Object Location for slot 5 with error code 3859
18.10.21 12:32:34.586 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Equipment Identifier for slot 5 with error code 3859
18.10.21 12:32:34.586 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Application Device Address for slot 5 with error code 3859
18.10.21 12:32:34.586 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Failed to read Axioline module info data for slot 5
18.10.21 12:32:34.592 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Vendor Name for slot 6 with error code 3859
18.10.21 12:32:34.592 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Object Location for slot 6 with error code 3859
18.10.21 12:32:34.592 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Equipment Identifier for slot 6 with error code 3859
18.10.21 12:32:34.592 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Application Device Address for slot 6 with error code 3859
18.10.21 12:32:34.592 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Failed to read Axioline module info data for slot 6
18.10.21 12:32:34.597 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Vendor Name for slot 7 with error code 3859
18.10.21 12:32:34.598 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Object Location for slot 7 with error code 3859
18.10.21 12:32:34.598 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Equipment Identifier for slot 7 with error code 3859
18.10.21 12:32:34.598 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Application Device Address for slot 7 with error code 3859
18.10.21 12:32:34.598 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Failed to read Axioline module info data for slot 7
18.10.21 12:32:34.605 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Vendor Name for slot 8 with error code 3859
18.10.21 12:32:34.605 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Object Location for slot 8 with error code 3859
18.10.21 12:32:34.605 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Equipment Identifier for slot 8 with error code 3859
18.10.21 12:32:34.606 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Application Device Address for slot 8 with error code 3859
18.10.21 12:32:34.606 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Failed to read Axioline module info data for slot 8
18.10.21 12:32:34.610 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Vendor Name for slot 9 with error code 3859
18.10.21 12:32:34.611 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Object Location for slot 9 with error code 3859
18.10.21 12:32:34.612 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Equipment Identifier for slot 9 with error code 3859
18.10.21 12:32:34.612 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Application Device Address for slot 9 with error code 3859
18.10.21 12:32:34.612 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Failed to read Axioline module info data for slot 9
18.10.21 12:32:34.617 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Vendor Name for slot 10 with error code 3859
18.10.21 12:32:34.618 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Object Location for slot 10 with error code 3859
18.10.21 12:32:34.618 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Equipment Identifier for slot 10 with error code 3859
18.10.21 12:32:34.619 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Axio - PDI Read: Failed to read Application Device Address for slot 10 with error code 3859
18.10.21 12:32:34.619 Arp.Services.Wbm.LocalBusDiagnostics ERROR - Failed to read Axioline module info data for slot 10
[/code]
[/code]
This doesn't look like any known issue with FW 2021.6, so upgrading the firmware probably won't help in this case.
Are you able to give us a complete list of I/O modules that are connected to the PLC in this case?
(a screen-shot of the "Axioline F" branch of the project tree in PLCnext Engineer will be fine).
here is:
I notice that you have configured 8 slots but the PLC tries to contact 10 slots. Maybe not the correct version of your project is downloaded to the PLC?
The drops in values might be caused by a power supply issue.
1. are UL and UP supplied by seperat supplys?
2. is the supply delivering up to 4 A?
or
some EMC troubles are the AI wires shielded?
What are you doing in your application?
Are you maybe changing the Module configurations dynamically during the runtime?
kind regards,
Oliver Warneke
Firts of all, thank you so much for your answer.
You are right, we have now 8 slots (two 4 Axionlane F backplane) at the beginning we have 4 + 6 Axionlane F backplane. The PLC logs belongs to this initial siuation. The correct project version is downloaded to the PLC.
Regarding a power supply issue:
1.- We can try to separate UL and UP.
2.- We also can check it.
In attachement there is a pic with the configuration of the Modules, if it helps: Can we know if we are changing the Module configurations during runtime?
Thank you so much,
Iván Valbuena.
To answer your question:
If you aren't changing the module configuration deliberately in your application at run-time, then you're probably not. :-)
(this is only possible using some advanced features).
Please let us know if the power supply adjustments change the result.