RTC (Real Time Clock)
Hello engineers on commnunity ! So i have the problem when i approach with RTC , which is not true with the current time , i tried reset the" Factory reset " , it's still not working, how can i fix it ?
Regards.

Regards.

Comments
If you are online with your controller, you can go to the controller name in the project tree (in your screen shot, it is called AXC F 2152 located right below the word "Project"). Double click this.
On the "Cockpit" page, there are a number of icons across the top.
In the middle of the icons, there is a clock with a "right" arrow.
If you click this, it will write the time to the controller.
PS: I was going to paste a screen shot to show you, but I'm still looking at how to paste an image in this response.