AXC F 3152 Led BOOT Blinking eight times

Hello

Mi name is Rodrigo Salas (company Rodotecnia) from Chile (SouthAmerica)

Someone gave me a 3152 PLC (which didn't work), and the problem is as follows:

The problem is that once the PLC is energized, no LED lights up for the first 25 seconds or so, after that the BOOT LED blinks 8 times, then goes off, and then everything is off again.

I reset everything with a HARD RESET, but the error persists.

I tried without SDCARD for fear that it could be ruined.

Does this problem have a solution?

Comments

  • Hi Rodrigo.

    Please try the Type 2 reset procedure detailed on Page 35 of the user manual:

    Please note:

    • The AXC F 3152 has a capacitor that may maintain power to the device for up to one minute after external power is removed. Therefore, when performing the Type 2 reset, you should wait for at least one minute before applying external power with the RESET button pressed.
    • After the RUN and FAIL LEDs light up, you will need to continue holding down the RESET button until all LEDs (except the E and D LEDs) light up. This might take 30 seconds or more.

    If this procedure fails to restore the controller, please contact the technical specialists in Phoenix Contact's office in Santiago. They are already aware of this discussion.