Hello,
I know there are variants of this issue already answered but I cant figure out how to manage mine specifically.
My need is when the user presses a button on the HMI I want my C# Program to overwrite a specific file ("myReport.txt") in a specific file path and then download that to the device that pressed the button.
My problem though is that when I try to use "File.WriteAllText(filePath, textData);" on the paths mentioned in the previous solutions, then my plc produces an error. Maybe there is a problem with the write permissions?
Also, I do not care if a user with no access can download the file but I do not want to compromise the security of the project solution + C# code that is running on my PLCnext.
Is that possible? Any ideas?
Thank you in advance.
Comments
Hi.
Am I right in saying that there are two independent issues here?
For the first issue: What path(s) are causing errors? Can you give more details of what the error looks like?
For the second issue: What method are you using to transfer the file to the HMI device?
Hello,
I do not think they are independent, because with a valid filePath I can write to the PLC but I do not think that that filePath will be a valid path that can be stored a file to be downloaded.
I used the following filePath because this is the one that was used in the previous answer for the file to be stored to.:
public const string reportFilePath = "/projects/PCWE/Services/Ehmi/ehmi/myReport.txt"; // ../opt/plc/XXX is the base path
That provided the following error:
IF I use -> public const string reportFilePath = myReport.txt"; // ../opt/plc/XXX is the base path THEN the file is created correctly but I do not think that I can use this file path to download it afterwards.
I haven't yet used a method to transfer the file to the device from which the user clicked the HMI button.
I appreciate the swift answer!
Please try without the leading slash, which indicates that the path should start at the root of the directory tree (
/
), not from the current directory (/opt/plcnext/
)Alright, I feel embarrassed now, thank you Martin once again.
So, regarding the security issue:
Does this way of working around the problem cause any security issues regarding my project solution + C# code?
No, I don't think that Oleksandr's suggestion in that other conversation causes any security issues for the project.