Fail to upload the project to Touch Panel.
Hi, I designed the HMI using Visu + Express Which is Version 2.56 and it is connect to PLC Next Engineer 2023.9.0 using OPC UA. And The problem is i am trying to upload the project to
TP 6215-WHPS, but it says 'failed to uploead the target devie file \FlashDrv\VisuProject\Project1.visprj '. And Previous sentence says 'The upload/download manager (CETransfer.dll) is not updated on remote devie!' What is the solution and how can I update it?
Comments
Hello,
I believe you are using an older firmware version of that TP. I would suggest updating the FW to version 180.0 and this should fix the error.
The newest FW version is available on our website.
Let me know if you have any questions!