AXC2152 OPC UA server with Beijer X2 Hmi Panel
Hi,
The opc ua connection works when plc user authentication is disabled, and anonymous login is selected in the hmi panel opc settings.
However, I would like to use user name and password for login.
I have an AXC2152 with OPC ua server using marked variables. namespace is set to ip addresss.
The Beijer X2 HMI panel has the following settings.
When trying to import tags in Ix developer I get the "error: badcertificateuri"
Any advice would be greatly appreciated.
Comments
Hi, I think this problem can be solved by putting the server certificate in the Trust Store that the client software uses.
In UaExpert this can be done by selecting the "Trust Server Certificate" button during the connection process.
I don't know how this is done with the client software that you're using (sorry).