Where to find PLCnCli2019.3
I need the PLCnCLi 2019.3 for windows to build some older c++ projects in eclipse.
Previously I could download this from the website when I needed it, but the archive does not go back further than 2020.0.
Upgrading the firmware version with al required changes in the C++ project is to much of a risk and not really an option.
Does anyone has in the installation file of PLCnCLi2019.3 for windows or now where to download it?
Comments
I don't think you need a version that old.
The newer version of the CLI should work with the old version of the SDK just fine.
The SDK is what's linked to the controller firmware, not the version of PLCnCLI.
PLCnCLI version 2019.3 does not exist according to our database, version 2019.0 can be used however. To receive this version, please contact your local subsidiary, for the Netherlands this would be support@phoenixcontact.nl . The best practice would still be to update the PLCnCLI and code to the latest version (2024.0 LTS), which can be found on the AXC F 2152 product page under Downloads -> Software.
With kind regards,
Damian Bombeeck
Technical Consultant
IMA Technical Sales Support