PLCNEXT SUPPORT
Dear Experts.
I have 2 issues with AXC F 2152 PLCnext please.
- AXC F 2152 have 2-port RJ45. Can I use them separately? Each port one IP Network. If they are only switch mode, Can I using many IP network for AXC F 2152
- I need using IEC60870-5-101_104 from store( see picture). Is SD Card mandatory to come with it?
Best.
Comments
Hi.
BR
For the question about the SD card - if the app documentation is not clear on this question, then you can contact the developers of the app using the "Contact Developer" button that can be seen in your screen shot.
Thank for your response.
I don't know how to set many IP for PLCNext.
Can you guide to me.
Best.
#Oleksandr Guminskiy
How can I find /etc/network/interfaces and import into PLC.
Many Thanks
Hello.
This file is already exists on plc file structure, literary at /etc/network/interfaces
Use sftp or ssh client to Winscp / Pytty etc to deal with it. https://www.plcnext.help/te/Operating_System/Connecting_to_the_controller.htm
Also you have to enable root user to modify files in /etc directory. https://www.plcnext.help/te/Operating_System/Root_rights.htm?rhhlterm=root&rhsearch=root
BR