Inquiry Regarding Analog Module (AXL F EX IS AI8 HART XC 1F) Configuration for Binary Switching Sens

Dear Support Team,

I am working on integrating a binary switching sensor connected to the AXL F EX IS AI8 HART XC 1F analog input module. The sensor operates on a two-wire loop-powered system, outputting 8 mA (Low State) and 16 mA (High State). Since the module includes both normal analog inputs and HART-specific inputs, I would like your guidance on the optimal configuration within PLCnext Engineer.

Key Considerations & Questions:

  1. Best Input Selection & Processing:
    • Should I use a HART input or a normal analog input for a binary switching sensor?
    • If using a HART input (REAL data type required), should I manually process the mA signal into a BOOLin PLC logic using a threshold (e.g., >12.0 mA = TRUE)?
    • Does the AXL F EX IS AI8 module provide any built-in threshold or signal processing functions to automatically convert an analog (mA) signal into a binary state?
  2. MTP Designer Integration:
    • Since the sensor functions as a binary switch, should I use a BINMON block instead of ANAMON in MTP Designer?
    • Will this impact how the data is mapped or visualized in the PLC or HMI?

I would appreciate any guidance, or relevant documentation to help configure this setup correctly in PLCnext Engineer.

Looking forward to your support.

Best regards,

SHNB

Comments

  • Hello SHNB,

    I can say the following about the first point:

    For HART sensors, the HART inputs must be used.

    Otherwise the normal analog inputs are used.

  • The MTP standard describes 2 interfaces for the binary sensors: BinView and BinMon. BinView covers most cases.

    BinMon have some additional flutter detection functionality.

    For this type of interface a special modelling will be created. And also this are different visual objects.