Siemens software SIMATIC NET and AXC F 2152 can not communicate through OPC UA.
Hello ,
We are using Siemens software and AXC F 2152 to communicate through OPC UA.
Siemens software:SIMATIC NET V15 ,OPC SCOUT V10.
PLC: AXC F 2152 (2019.6)
In our test, we found that OPC SCOUT can communicate with AXC 1050, but only servers can be found when communicating with AXC F 2152, but data communication can not be established.
In addition, we found that OPC score does not support X509 certificate mode.
I know that AXC F 2152 OPC UA supports x509 certificates. Does AXC F 2152 only support x509 certificates, or does it support other ways? If it needs to communicate with Siemens software through OPC UA, is there any other way?
Thanks a lot!
Comments
picture
Hello,
Please see this discussion:
https://www.plcnext-community.net/index.php?option=com_easydiscuss&view=post&id=2318&Itemid=224&lang=en
In summary:
- Martin.
Hello Sir,
I've tested it, but I still can't set up normal communication. PLC has been powered off and restarted.
Hello,
I see that the Endpoint URL is
opc.tcp://axc-f-2152-1:4840
.Do you have a DNS server or a hosts file that maps this DNS name to the IP address of the PLC? If not, then please try changing the Endpoint URL to
opc.tcp://192.168.1.10:4840
. (or whatever the IP address of your PLC is).- Martin.
Hello Sir,
Changing the DNS name to IP can solve the problem, and 128/256 encryption mode can also be used.
Thanks very much!