Hi,
I have migrated a project to Plcnexteng 2022.0.1 LTS. In the project all network settings are set in automatic and when I change the settings in project all ip-addresses are changed to the same address.
In previous versions it worked fine and the last address byte where different.
Is this a known issue and can I fix it somehow? I have 153 pn-nodes in project
Br Stefan
Hello Stefan,
this Issue is not known and so far we were not able to reproduce it.
What PLCnext Engineer version was your project before the conversion?
And what IP Address Range was selected in the project settings etc. ?
Did you also replace/upgrade the controller template?
kind regards,
Oliver
Hello Stefan,
we were able to reproduce the issue.
We hope to fix this in PLCnext Engineer Version 2022.6.
For now the only solution to the problem is assigning IPs Manually.
Sorry about this.
kind regards,
Oliver
Hi,
Thanks for reply.
It’s good that you find the issue and will fix it in later release.
Br Stefan