Hello, how it is possible to setup the AXC-F 2152 simultaneously as a Profinet controller and as a device. A phoenix contact application engineer state out this thesis, because we planed this PLC in our project. But actually there is no possibility visible to to it. Hope for help - because the delivery date is near BR Andreas Ehrlich
Hello Andreas, It is possible with just the AXC F 2152 as long as both PN Networks are in the same Subnet. Or by adding the AXC F 2152 + ETH XT module you are able to run two seperate PN Networks (by IP and MAC.) PN Master MAIN (10.0.0.1) —> PNDevice AXCF 2152 (10.0.0.2) || XT ETH( 192.168.1.10) PNMaster ----> (192.168.1.123) PN BK Field Level.

Hello Oliver, thanks for your reply. Okay, from our actual project status it is possible to use for all devices, the same IP-area. So, please revise my thesis if it is wrong, the AXC F2152 can be used as a type of gateway to be a controller for profinet devices (e.g. at ethernet port X2) without S2 redundancy functions and publishes the captured data as a device in another profinet network with system redundancy S2 (e.g. a ethernet port X1)? In our actual project: The communication in the lower level profinet without SR2 is realized and tested. Thats ok, as I use the video description from the question (https://www.plcnext-community.net/en/discussions-2-offcanvas/i-need-some-help-to-communicate-plc-in-profinet.html). BUT here some clear questions: 1. My program writes the informations from the lower profinet devices in a defined order of data/variables. But how can I order these infromations, to provide these data for a master in a higher profinet network? 2. How can I setup the AXC-F 2152 with PLCnext Engineer as a profinet device in a SR2 configured profinet? Thanks. BR Andreas Ehrlich
Hello Andreas, let me try to answer your questions: [list=1] []The AXC F 2152 can be at the same time PN controller and device []The Controller defines the redundancy mode, so if the controller is S2 you only have to add the AXC F 2152 (or any other S2 compatible device) as device into the PN configuration [/list] More details on how the configuration, PD assignment and some other stuffs can you find in the PLCnext Engineer section from our Info CenterInfo Center. We also offer project and system consulting, if you like I can pass your contact details to our sales engineering team. Please let me know, Frank