AXC F 2152 with Analog Input - Wrong (analog) values

Hi, I have 2 laser distance sensors (SICK DT35) with analog output (0-10V). They are connected to the analog input channels 1 and 2 and the gnds are connected to common ground (each).
In a program I’ve setup 2 external variables UINT which are connected to process data item ai-1/ IN01 and 1i-2/ IN02.
In debugging mode, I can see that the values somewhat changes with moving the sensor around, but something weird happens: If I move one sensor and the other sensor is still, somehow it changes the values of the not-moving one. I’ve checked the linkage more than once and I don’t think that there is an electrical/ cable problem which does some weird disturbances.
However, I don’t know what it could be either. Maybe an overflowing buffer? Is the size of 16 bits correct for the ADC with 12 bits? Also, I cannot get to 10_000 mV, the max value is around 5xxx which is also weird since it is the 0-10V smart element.
Some ideas there? Thanks!

Hello robin4clx,

which AXL SE module are you using?
How are the sensor cables shielded?
Have you ever tried whether the behavior changes if you assign channels 1 and 3, for example?
We are not aware of any interference between the channels.
You can also contact support@phoenixcontact.de directly, where there is already ticket #448053 for your query.

Hi, I am using the 0-10V Analog Input module: SE AI4 U is the name I think.
Seems like it solved! The problem seemed to be related to the GNDs not being connected (of the sensors and the PLC).