AXC F 2152 with two device

Hello! Could you help? We try connection two device, 1st Siemens 300(ProfiNet), 2nd Yaskawa(Ethernet/Ip). Is it posible connect to AXC? If we connection Siemens AXC go to alarm… Protocol Ethernet/ip lost connection, bur Profinet start work.

Yaskawa MPiec as Ethernet/IP scanner works. Use these settings:

Yaskawa MPiec as Ethernet/IP scanner works. Use these settings:</p>[https://forum.plcnext-community.net/uploads/2829R43GA22R/image.png</a></p>

Thanks, parameters it’s ok. Question about somebody try connect to devices? Because if we use one devise(Siemens or Yaskawa) connection work, but if connect two device connection down.

We connect without modules only axc f…

It’s start work, but if first we connect EthernetIp, after loading we connect ProfiNet. If we reboot system, we have alarm from Yaskawa about gateway. Do you have ideas?)

It’s start work, but if first we connect EthernetIp, after loading we connect ProfiNet. If we reboot system, we have alarm from Yaskawa about gateway. Do you have ideas?)</p>

Go to the WebUI of the IEC controller and set the gateway to the same IP address range as controller. Typically set to 192.168.1.1. The alarm is clearable and won’t have any affect on function.