AXC F XT IB and Schneider Branch 170BNO

Hello! Will module AXC F XT IB work with Schneider Electric Branch 170BNO67100? SE Branch 170BNO67100 is made on the basis of a Interbus chip SUPI2.

Now the error appears constantly - 0BDF.

Hi Maxim, the AXC XT IBS is using a IPMS4 Master and can only support IBS devices with at least SUPI3.

Means the older SUPI2 modules can not be used with the Master. Please refer the restrictions in the datasheet. The Profinet/Interbus Proxy FL NP PND-4TX IB could be an interesting alternative.
It is using the IPMS3 which supports also SUPI2 and other nice IBS features (fiber diagnostic, fast switching …) Take care, Frank