Axioline Error

Hi, after downloading the program to my AXC F2152 Controller and starting the program I get this error message: Axioline State Chnaged: RDY BUS FAIL (0x0084), ErrorCode=0x0x02, AddInfo=0x0004 I have only connected a TP6070 from Phoenix and no more. How can I get this error solved? Thanks Michael

Hello Michael, please send me the detailed information: 1. Used PLCnEng Version 2. PLC-Type and used FW I assume the cause of this failure is the old PLCnEng version. Is it possible to update the PLCnEng to Version 2021.6 and the PLC FW to 2021.6 (if this Versions are not current)? Thanks & Best Regards Eduard

Hi Eduard, PLCnEng 2021.6 AXC-F2152 FW 2021.0.3 LTS How can I make the firmware update? Regards Michael

Hello Michael, please find the description under following Link: https://www.plcnext.help/te/WBM/Administration_Firmware_Update.htm Best Regards Eduard

Hello Eduard, I have done the firmware update, but the BF LED is blinking all the time, I have only connected the Phoenix TP6070 Panel and I do not need any other BUS. Thanks Michael

Hello Michael, I assume in your case the BF-D-LED is blinking with 1Hz. If it’s behavoir, please see the description in the User Manual „3.9 Diagnostic and status indicators“. Status of PROFINET communication: Link status present, no communication connection to the PROFINET controller Please note, the Phoenix TP6070 Panel is not the PN-Device and don’t supports the PN-Communication. You can deactivate the PN-Controller and Device functionality via WEB-Interface to deactivate the PN-Component and PN-Status-LED’s (see attached Screenshot). Please note after PN-Deactivation it is not possible to change the IP-Address via DCP (e.g. in Tools: PLCnext Engineer or NetNames+) Best Regards Eduard