I would know when the Library Modbus RTU will be update in the store, in order to use an AXL F SE RS 485 and AXC F 2152 Fw 2020.0. Thanks. Ciao
I was about to upgrade to 2020.0 until I saw this post. I have the same concern. But, do we need to upgrade this librarie anyways ? If so, when the new package will be available ? Thanks
Hi, I’ll clarify this and come back to you both asap. cu Frank
Hi together, it´s great if you want to use our Smart Elements. The AXL SE RS 485 isn´t integrated and tested for the Modbus RTU library. But the structure of the AXL SE RS 485 and the AXL F RS UNI 1H in the process data is the same base. Which means, that the AXL SE RS 485 in theory will work with the Modbus RTU library 2. Because the AXL SE RS 485 does support the mode “transparent” the Input of the function block „xAuto_CRC“ must be “FALSE”. My colleagues will test the combination in detail - but it´s actually not planned. They will do it by the way. Best regards Stefan
Hello together, the Modbus RTU library for PLCnext Engineer for the AXL SE RS 485 is available now. https://www.plcnextstore.com/#/215 Best regards Stefan