AXL1152 cannot see any modules on bus(0x0284)

Hello,

Due to delivery times Phoenix have provided me with a loan PLC(1151412), Can module(2702668) and IO(2701916), although helpfully the IO module doesn't have the black power input block attached.

I am trying to get my first project with PLCNext, a CAN project talking to a linear actuator, up and running.  However the AXL1152 can not see any modules on the bus and is giving error 0x0284, which doesn't seem to appear in the diagnostic manual as a code.

Can anyone help me get this sorted?

Jon

Ok, so I got that figured out, the controller seemingly doesn’t like unpowered modules sat on the bus line. Now LED D on the 2702668 is flashing, not on constantly which seems to be fine. But I can’t communicate with the device even using the example Phoenix program for J1939 that I downloaded with library from the store.

Has anybody done J1939 previously?