Cannot connect to EPC 1502

Hi,
I set the default routing of epc 1502 to be WLAN but now I cannot access it through the wifi network. When I try the two ethernet ports I am unable to connect. I tried SSH, the WBM and PLCnext engineer cockpit but none of them give access.

I think my best option would be to reset to default setting. How can I go about resetting?

If there is another solution I’d appreciate it.
Thanks in advance
Sam

Here is an answer from the EPC support team:
A factory reset from external can not be done with this hardware. Some kind of connection is required (SSH). If you are running Firmware 2022.0 LTS, you could try installing a Monitor via DisplayPort to the EPC. To do so, shut off the EPC, install any DIsplayPort-Monitor and power-on the EPC again. If the device still functions, the Web Based Management should be shown. If that is the case, please install a USB mouse and keyboard to your EPC, log into the WBM and make sure you haven’t defined two interfaces into the same subnet (for example the configuration X3 - 192.168.1.10 & X2 - 192.168.1.11 are not allowed and can cause errors.) Could you also try to ping the device on the other ETH-interfaces that you were not using? (default: X3 - 192.168.1.10) (default: X2 - 192.168.2.10) If this is unsuccessful, you should contact your subsidiary or after-sales service directly.