Can't connect to plcnext's OPC UA server via private key in UA Expert

I need to connect to my OPC server on PLCNext AXC F 2152. I can do it with credentials but when i use certificate and private key - UA Expert sends me: “Error ‘BadConfigurationError’ was returned during ActivateSession”.
I got the certificate and private key from PLCNext Controller via SSH in folder /opt/plcnext/Security/IdentityStores/OPC UA-self-signed. I didnt found any documentation where i can find private key else. I also validate them using:
“openssl x509 -noout -modulus -in certificate.pem | openssl md5” - for certificate
“openssl rsa -noout -modulus -in key.pem | openssl md5” - for private key
the output value was the same
In OPC settings of my project i have set “Certificate” field to Self-signed by controller and download the project to plc. I also added some ip-addresses to avoid “BadCertificateHostNameInvalid” error
Finally i convert certificate.pem to certificate.der using online tools and then trying to connect to opc server using UA Expert:
image.pngWhen i connect i get:
image.pngAfter “Continue” i get no errors to ignore but in logs it sends me this:
image.png

Currently the OPC UA server only supports the “Username/Password” authentication method, or “Anonymous” (if security is completely disabled in the PLC - which is not recommended).
There are plans to allow Certificate-based authentication in the future, but there is currently no timeline for this.