Delete project sources in the plc

I downloaded the project sources to the plc to allow other programmers upload capability. The project is now complete and we would like to not provide the sources to our customer. Is there a way to delete the project sources in the plc so it can’t be uploaded.

node-red.pdf

Hello Gian, as soon as you download the project without sources the projectsources will be gone from the PLC. you can make sure by checking like this: root@axcf2152:/opt/plcnext# find . -name "*pcweax" ./projects/PCWE/Src/Test.pcweax ./backup/PCWE/Src/Test.pcweax