DHCP address on 2152

On the 2152 controller we have made an MQTT client which connects to an online broker.
Now this PLC is placed in a random network of a customer where we have no information about this network and IP range.

Because there are multiple PLC`s, and different customers, we cannot set an fixed IP address per project.

I read that it should be possible to set the PLC to get it`s local IP address via DHCP?
There is an option to configure a start and end IP address, but even then it must be in the same range. (not possible to set it to 0.0.0.0 to 255.255.255.255
I also don’t see this DHCP option in my PLCnext engineer version.
PLCnext engineer 2023.0.1, CPU is a 2152 with FW 2023.0.0

How can i configure this?

Hello!
I think, that one of the ways of provide this task is related to general linux administration proposes.
уес.PNG
* Ensure you have root account with password enabled via “sudo passwd root”;
* Login as root
* Edit /etc/network/interfaces like noted below
*
Of-course, you don’t want to loose static assess to plc completely, so in folder /etc/network/if-up.d you have to create file add_ip.sh with next content (name of file can be any suitable for you)
* Content of file:
#!/bin/sh
ip addr add 192.168.1.10/24 dev eth0
Don’t forget allow it’s execution via chmod +x add_ip.sh
* Reboot your plc
This steps will provide both automatic dhcp settings and additional static point to eth0 of your plc.
Best regards

Important notice!
Profinet device and Profinet controller system services mast be deactivated to prevent fatal errors during startup, that cause stop of MainProcess.
Best regards

It’s also possible to make this setting from PLCnext Engineer:
image.pngNote that the settings in the “Online Parameters” tab are not transferred to the device with the PLCnext Engineer project, but are only transferred to the device when the “Write” button is pressed (the little gear wheel with a pencil).

I will suggest another alternative that I’ve found success with. Starting with FW2023.0, I had issues with the methods suggested by and . The gateway address acquired through DHCP was not acquired correctly. The method I use now is to call a command to the linux shell using the PBCL_SysLinuxShell from the PLCnextBase library.
Using the command “sudo dhcpcd ” - replace with eth0 for AXC F 2152 or lan1 for AXC F 3152. This will acquire a second virtual IP address for the network interface, leaving the original static IP definition intact. This does require modifying the sudoers file to add permissions for the plcnext_firmware user. I add the line: “plcnext_firmware ALL=(ALL) NOPASSWD: /sbin/dhcpcd”.
This may not be the simplest or supported method, but the advantage I found is I can call this command again to refresh the DHCP lease without rebooting.

I will suggest another alternative that I’ve found success with. Starting with FW2023.0, I had issues with the methods suggested by [@Oleksandr Guminskiy</a> and [@Martin PLCnext Team</a>. The gateway address acquired through DHCP was not acquired correctly. The method I use now is to call a command to the linux shell using the PBCL_SysLinuxShell from the PLCnextBase library. </p>Using the command "sudo dhcpcd " - replace with eth0 for AXC F 2152 or lan1 for AXC F 3152. This will acquire a second virtual IP address for the network interface, leaving the original static IP definition intact. This does require modifying the sudoers file to add permissions for the plcnext_firmware user. I add the line: “plcnext_firmware ALL=(ALL) NOPASSWD: /sbin/dhcpcd”. </p>This may not be the simplest or supported method, but the advantage I found is I can call this command again to refresh the DHCP lease without rebooting.</p>

Nice and flexible suggestion in various cases.

Hi
Thank you, it seems that fw version 2023.0.0 does not accept the dhcp setting by plc next engineer.
I have changed dhcp in /etc/network/interfaces as you described.

if I understand correctly i need to create a file named ‘add_ip.sh’ in the folder /etc/network/if-up.d
With content of file:

#!/bin/sh
ip addr add 192.168.1.10/24 dev eth0

But what do you mean by:

                              * Don't forget allow it's execution via chmod +x add_ip.sh

Do i need to excecute this command from root user or set this command somewhere?

I will suggest another alternative that I’ve found success with. Starting with FW2023.0, I had issues with the methods suggested by [@Oleksandr Guminskiy</a> and [@Martin PLCnext Team</a>. The gateway address acquired through DHCP was not acquired correctly. The method I use now is to call a command to the linux shell using the PBCL_SysLinuxShell from the PLCnextBase library. </p>Using the command "sudo dhcpcd " - replace with eth0 for AXC F 2152 or lan1 for AXC F 3152. This will acquire a second virtual IP address for the network interface, leaving the original static IP definition intact. This does require modifying the sudoers file to add permissions for the plcnext_firmware user. I add the line: “plcnext_firmware ALL=(ALL) NOPASSWD: /sbin/dhcpcd”. </p>This may not be the simplest or supported method, but the advantage I found is I can call this command again to refresh the DHCP lease without rebooting.</p>

Hi
Thank you,

I`m not fammiliar with the commands, what do you mean by:
This does require modifying the sudoers file to add permissions for the plcnext_firmware user. I add the line: “plcnext_firmware ALL=(ALL) NOPASSWD: /sbin/dhcpcd”.

Can you give me some more information?

Hi [@Oleksandr Guminskiy</a> </p>Thank you, it seems that fw version 2023.0.0 does not accept the dhcp setting by plc next engineer.</p>I have changed dhcp in /etc/network/interfaces as you described.</p>if I understand correctly i need to create a file named ‘add_ip.sh’ in the folder /etc/network/if-up.d</p>With content of file:</p>-----------------------------------------------------------------------</p>#!/bin/sh</p>ip addr add 192.168.1.10/24 dev eth0</p>-----------------------------------------------------------------------</p>But what do you mean by: </p>
* Don’t forget allow it’s execution via chmod +x add_ip.sh</li></ul>Do i need to excecute this command from root user or set this command somewhere?</p>

Hello!
Script placed at /etc/network/if-up.d will execute automatically during system startup, when eth0 successfully started.
And yes, you have to make this operation under root acc, otherwise system will decline commands.
Command “chmod +x /etc/network/if-up.d/add_ip.sh” will set special bit of file, that will allow it’s execution as script file.

It’s also possible to make this setting from PLCnext Engineer:</p>[https://forum.plcnext-community.net/uploads/5AM1575JO7IF/image.png</a></p>Note that the settings in the “Online Parameters” tab are not transferred to the device with the PLCnext Engineer project, but are only transferred to the device when the “Write” button is pressed (the little gear wheel with a pencil).</p>

Hi ,
Unfortunally this function didn`t work.
I have dis-abled the profinet in WBM, and set DHCP by PLCnext Engineer, online parameters and then the write button.
When PLC is restarted, again the PLC remain the static IP.

[https://forum.plcnext-community.net/discussion/comment/11922#Comment_11922</a></p>Hi [@Rob H</a> </p>Thank you, </p>I`m not fammiliar with the commands, what do you mean by:</p>This does require modifying the sudoers file to add permissions for the plcnext_firmware user. I add the line: “plcnext_firmware ALL=(ALL) NOPASSWD: /sbin/dhcpcd”.</p>Can you give me some more information?</p>

Linux commands executed via the PBCL_SysLinuxShell from the PLCnextBase library are executed with the plcnext_firmware user. To execute the dhcpcd command, the plcnext_firmware user needs rights to execute as root without providing a password. Doing so requires adding a rule to the sudoers. For help on adding users to sudoers, I am not the expert. There are resources out there for that. A short description of what worked for me:
SSH as root user. Use command sudo visudo /etc/sudoers.d/axcf2152-sudoers to begin editing the sudoers file. Add line plcnext_firmware ALL=(ALL) NOPASSWD: /sbin/dhcpcd Then after a reboot, dhcpcd should be able to be executed from the PBCL_SysLinuxShell function block.

[https://forum.plcnext-community.net/discussion/comment/11949#Comment_11949</a></p>Linux commands executed via the PBCL_SysLinuxShell from the PLCnextBase library are executed with the plcnext_firmware user. To execute the dhcpcd command, the plcnext_firmware user needs rights to execute as root without providing a password. Doing so requires adding a rule to the sudoers. For help on adding users to sudoers, I am not the expert. There are resources out there for that. A short description of what worked for me:</p>SSH as root user. Use command sudo visudo \/etc\/sudoers.d\/axcf2152-sudoers <\/code>to begin editing the sudoers file. Add line plcnext_firmware ALL=(ALL) NOPASSWD: /sbin/dhcpcd </code>Then after a reboot, dhcpcd should be able to be executed from the PBCL_SysLinuxShell function block.</p>

Hi Rob
I’m trying it your way but I’m a litlle stuck. I opened the sudoers file ( see image), but I don’t know how to edit/save it.
Can you help me out?
image.png

The default editor for visudo is vim so you can certainly find more help on using the editor on the web. To help with your immediate problem:
To save and exit
:wq
To close without saving:
:q!

The default editor for visudo is vim so you can certainly find more help on using the editor on the web. To help with your immediate problem:</p>To save and exit</p>:wq</p>To close without saving:</p>:q!</p>

Thanks I edited the file and rebooted the controller. A few questions:
Do I have to turn off the profinet controller option in WBM?
How do i know this works/ know the dynamic IP?
Does the execute for the function block need to stay true?
And the FB gives following result:
image.pngThanks in advance!