Hi all,
While updating our HMI I encountered an unsuspected behavior of the image button up / down property in PLCnext Engineer in combination with an AXC F 2152.
If I assign a Boolean (either local or external) and provide a HMI tag for a webpage. Any button assigned to it will first display the image up picture and after pressed will display the image down picture. But when pressed again (and Boolean toggles again) the image down image still persists. I expect the image up picture to be visible again.
This is with a latching button property. If it is not latching, then the image up picture is displayed again when releasing the HMI button.
Am I correct in this assumption that this is not the expected behavior (and thus a bug?)
I take a look at problem, that Daniƫl noted, and find out that this situation occur since PLCNext Engineer 2022.9, and pass through 2023.0.3 LST and 2023.3.
PLCNext Engineer 2022.6 work fine in described situation.
Best regards.
Thank you Oleksandr for checking with other versions. I have submitted the bug to support @ Phoenix Contact so it will be dealt with in an update of PLCnext Engineer.
Hi, it seems that PLCNext Engineer 2023.6 solve this issue.