I'm trying to communicate a ET200SP with a AXC F 2152 with safety integrated (AXC F XT SPLC 1000) using GSDML-V2.35-Phoenix Contact AXC F 2152-V1.0-20210811 in TIA Portal V15.1. Do you have some example or documentation how to do that? For us is clear how it works in TIA Portal but not idea how to configure this communication in PLCNEXT Engineer.
Thanks.

Hello, there’s a specific GSDML on the homepage, which you already have.

In the project you can plug a virtual 8-bytes safety device additionally in slot 2 and do the profisafe addressing as at any other device. The safe IO-Data can be used in the program, as well as the non-safe IO-Data from the 512-bytes-slot.​
​​

I am at your disposal for further questions!