How add AXC F 2152 as device profinet

Dear mates. I have issue when i try connect AXC F 2152 as profinet device and i want know how do it. I do the nexts steps:

                                               1. In AXC F 2152 only write in pnd_output some data for see in a Siemens S1516.
                                               2. In Siemens S1516 IDE(TIA Portal) load gdsml file downloaded from AXC F 2152 page.
                                               3. Add module AXC F 2152 and connect to S1516 in TIA Portal.
                                               4. I configure module with parameter of AXC F 2152 and load program in S1516.

S1516 give me a error fot not found AXC F 2152 PLC. There is some that i do wrong in AXC F 2152? Thanks for advance.

Hello, did you assgin the PN Name to the PLC coressponding to the name used in the Tia project?

I try assign a name but TIA portal not found PLC next. I check the AXC IP but is correctly. I try conect to PLC or Tia portal PC and can’t found device for assign name.

Hello,

here some things to check:

                                               * are the BF-C and BF-D LEDs on your PLC flashing?
                                               * which FW Version is installed on the PLC
                                               * can you ping the PLC from the TIA PC?
                                               * you can also use PLCnext Engineer to assign the Name you used in TIA maybe you can avoid the problem of the TIA PC not finding the Device.

kind regards, Oliver