How to replace the hardware in PLCnext Engineer?

Hello: The context menu “Replace” of PLCnext Engineer is always grey for controller or module in version 2019.3 or 2019.6. I update the PLCnext Engineer and the firmware of the axc f 2152 from 2019.3 to 2019.6. Then I use PLCnext Engineer(2019.6) opened a program designed by PLCnext Engineer(2019.3) and updated the program. But I can’t replace the controller from axc f 2152(FW 2019.3) to axc f 2152(FW 2019.6) in the program. who can tell me how to replace controller from axc f 2152(FW 2019.3) to axc f 2152(FW 2019.6) in the PLCnext Engineer. Thanks a lot.

Hello, Right-click on the new PLC type (in the Network → Axiocontrol → Devices → Controller section of the Components pane) and select “Copy”. Right-click on the current PLC instance and select “Replace”. (or drag and drop) Martin.

Hello Martin: Thank you very much!

Hi Chenshijn, there is also a FAQ for this, please check the following link. How to replace the controller template Take care!

Dear all, Just tried to update my current project by changing the version of the controller. I choose the latest one available, copy, and on the current controller, on right-mouse click, i choose the option replace. That action is started, but fails. On the right lower corner there comes a message: ‘The operation could not be executed’. Why? There nothing in the log’s. Please help. Kind regards, Wilco

Oops ? The the AXF F 2152 controllers are listed twice… I had chosen the wrong one. Regards, Wilco

Yes, in fact there are currently 8 variations of AXC F 2152 listed in the latest version of PLCnext Engineer … But, as you have found, it is important to select the one that matches your controller. ~ Martin.