Hello, I need two network, one for internet and aother for device. So I add a extended module AXC F XT ETH 1TX - 2403115. I assinged an IP for the AXC F XT ETH 1TX - 2403115 in PLCNext Engineer, but it not worked. I check the IP with ifconfig and find the enp1s0 all ways is the default setting"192.168.2.10". How can I use the AXC F XT ETH 1TX - 2403115. Best Regards.
Hi, I have a big problem when I try to use the AXC F XT ETH 1TX. When I add AXC F XT ETH 1TX to the AXC F 2152 left side, all the PN device lost connected, if I removed the AXC F XT ETH 1TX, Everything is back to normal. Can you help me? Thank you! Best Regards!
Hello Chenshijin, the XT ETH module will be configured as the PN Controller by Default. when configured. If you want to assign an IP address to the XT ETH best use the PN IP assgining tools in the PLCnext Engineer ,NetNames or some other DCP tool.
kind regards,
Oliver
Hi Oliver, Thank you for your reply,It’s very useful to me. I use the NetNames+ assigned an IP for the AXC F 2152 or XT ETH, but when I repowered the device’s IP is returned to previous IP address. Best Regards!
Hello, You need to check the option shown below. Regards,
Martin.
Hi Martin, Thank you very much! It is working. Best Regards! Chen Shijin