Hello, I expect it to be an easy question but I can’t figure it out. I have an AXC F 2152 plc with 3 analog input cards the AXL SE AI4 I 4-20mA (1088062), AXL SE AI4 u 0-10 (1088104) and the AXL F AI4 U 1H (2688501). I do get an input in the plc from card 2688501, but nothing at all from 1088104 and 1088062. I’m sure there is voltage or current on it. i have tried with WORD, DINT, UINT, REAL. I don’t get any value out of it at all. what could i have done wrong? Online the maps do not indicate an error. I hope someone can help me. thanks already.
It might help if you show images of your configuration.
I noticed the modules that are not working are AXL SE. What is the state of the LEDs on the SE backplane (AXL F BP SE4 or SE6)?
If you go to the WBM for the AXL 2152, there is a page that shows the state of your local bus (see screenshot). Do you have any diagnostics that may indicate an error?
SFW
Hi Steve, thank you for your comment. yes indeed the AXL SE analog modules doesn’t work. I also have installed a AXL SE Digital module which works fine. I have an AXL F BP SE4, all leds flashing green, and the up lights is green. On the AXC F 2152, LED BF-D is flashing red. I have included a screenshot of diagnostics. I didn’t think I had a error, but I haven’t been working with the plcnext for very long.
Hello , can u resolve this problem? I have the same problems whit the 4 modules in the PLCNext kit.
Please tell me if you hade resolved?
Thanks!
HELP!!!
Hello! I have a similar problem. I have an AXC F 2152 PLC with three AXL F BP SE6 module carriers connected to it. After loading the project, the module LEDs on the AXL F BP SE6 units start flashing. Seventeen AXL SE DO16/1 modules and one AXL SE DI16/1 module are connected to the AXL F BP SE6 carriers. If I remove any single AXL F BP SE6 unit, all the others start working normally.