Is it posible to run the IEC 60870-5-104 Protocoll over the XT-ETH-communication card?
Dear Customer,
Yes, it is possible to operate the IEC 60870-5-104 protocol via the AXC F XT ETH 1TX extension module without any issues.
Please follow these steps:
-
Configure the expansion module
In PLCnext Engineer, add and configure the AXC F XT ETH 1TX PLC extension module and assign a valid IP address to the module.
-
Bind the communication to the XT-ETH interface (optional)
If you want the IEC 60870-5-104 communication to use only the XT-ETH module, enter the module’s IP address in the input parameter
IN_LS15_BindIpof the functionReSy10x_ConnectMgTcpV06.If this parameter is left empty, the controller can be accessed through all available network interfaces.
-
Configure the IEC 60870-5-104 connection
Set up the communication interface and configure the required IEC 60870-5-104 objects according to your application requirements.
-
Check the license
Please make sure that the required IEC 60870-5-104 license is installed and activated on the controller.
-
Download the project
Once the project has been downloaded to the controller, the communication should start operating as configured.