IEC61850 Client in smart RTU

Dear Sir/Madam.
I’m testing Smart RTU as IEC61850 to connect to protection Relay.
In document, I saw that smart RTU can work as IEC61850 client.
But, in webserver of smartu RTU i see only configuration as IEC61850 server.
I wonder that what I mistoke?
Please support me.
Many thank.

Hello ,
the IEC61850 client function is available in the SMARTRTU AXC SG from FW V01.09.00.02. Please update your device to this version. Than it will look like this:

Link: https://www.phoenixcontact.com/de-de/produkte/fernwirkgeraet-smartrtu-axc-sg-1110435
Regards

Hello ,</p>the IEC61850 client function is available in the SMARTRTU AXC SG from FW V01.09.00.02. Please update your device to this version. Than it will look like this:</p>[https://forum.plcnext-community.net/uploads/A9CCSM46OLSP/image.png</a></p>Link: [https://www.phoenixcontact.com/de-de/produkte/fernwirkgeraet-smartrtu-axc-sg-1110435</a></p>Regards</p>

Dear Sir
Thank for your instruction.
I updated firmware and saw IEC61850 client configuration.
I have an addition issues please.
In Smart RTU , How I can Monitor connection State between Smart RTU and partner Devices?
Example Smart RTU connect to IEC61850 relay via LAN cable. When Relay lost power supply or any other problem cause lost connection t Smart RTU. How Can I monitor it on smart RTU?