Dear Community, During our quality analyses we have identified a possible critical behavior after a firmware update to FW 2021.0. Under certain circumstances, an invalid project configuration may occur on the controller after a firmware update.
In this case, the controller cannot start the project and further project downloads are rejected. Typical footprints are as follows:
* The "Fail" gets active directly after the FW update were performed and succeeded. * It is not possible to deploy a new project via PLCnext Engineer. * The Output.log (/opt/plcnext/logs/) does show the following exceptions.
ERROR - Exception occurs while loading plc component 'Arp.Plc.Esm': Exception of type 'Arp::System::Commons::InvalidConfigException' was thrown
`**Task ‘Globals’ already defined.**`or
ERROR - Exception occurs while loading plc component 'Arp.Plc.Esm': Exception of type 'Arp::System::Commons::InvalidConfigException' was thrown
**Task 'ServiceTask' already defined.**Remedy: The cause of the issue is a change in the way some system internal tasks were configured.
Under special circumstances, a duplicate configuration may occur in the overlay file system.
This can happen if, for example, the project folder /opt/plcnext/project has been manually copied to the controller or if a download change operation were declined. In any case will the following options resolve the fault:
1. Perform a factory reset via PLCnext Engineer (Cockpit)
2. Perform a factory reset type 1 via ssh (Factory Reset)
3. Delete the following files in the /upperdir/
After restarting, does the control boot at least in ready mode and a new project can be deployed. We will release in the next weeks the Hotfix 2021.0.2 which will prevent the described problem. We apologise for the inconvenience.