Issue with ModBus communications on 2152 + RS485

I am having a timeout error communicating with a modbus sensor. I am using PLCnext Engineer 2023.0.5 Build 6.0.416.0 Rev f248e370. I am trying to use the ModBus_RTU_13 Library on a AXC F 2152 with an AXL SE RS485 to read data from a temperature and humidity sensor. I have checked my serial parameters are matching, but I’m not sure if there is something else I am missing?
Capture1.PNG

I am still having this issue, I am attempting to send and receive data from a valve, and I have created a buffer to track the changes of the diagCodes for the function block I am using. I can see the TX light flash only once a cycle Can I get some feedback as to how to resolve this issue?
The last four diagCodes I recorded are: 16#8300 0000 , 16#8000 0000 , 16#C110 0001 , 16#8300 0000
Capture2.PNGCapture3.PNG

I have figured out the issue here;

                              * addressing should be 2 instead of 40002 etc,
                              * FC23 not working, swapped it out for FC6 and FC3
                              * double check 485 wiring polarity

I’m able to monitor and control Modbus devices now