Modbus RTU Slave Input Register Limitations (Modbus_RTU_12 Library, MB_AXL_SE_RS485_Slave_3)

Hi all,
Is there a limitation with using the Modbus_RTU_12 library to implement a Modbus RTU Slave using block MB_AXL_SE_RS485_Slave_3 that you are limited to Input registers with addresses between 2000 and 2009? I would like to use just 2 Input registers, addressed 30003 and 30004, but with using this block it only seems that I can use addresses 32000-32999.
I have a device (fuel management system) that is connected to my AXC F 2152 via a AXL SE RS485 card, which has the following settings that cannot be changed:

                                          * Baud rate: 9600
                                          * Data bits: 8
                                          * Parity: None
                                          * Stop bits: 1
                                          * Sends a command to read the input register once every couple of seconds (slave id 01, function code 04, start register 02, number of registers 02) 

Any help would be much appreciated!

Hello,
the FB MB_AXL_SE_RS485_Slave_3 have a fix range from 2000-2999 and can not be change .