Hello, I’m trying to use the modbus server from library Modbus_TCP_9. We try to replicate an existing device which uses address ranges for holding registers up to 9000+. When, from the client, I try to read the registers, I get illegal data address. In the doc of the library it states that the range for holding registers is 0-65535. However everything above 7167 is not readable (illegal data address). Is there a setting somewhere to be set in order to allow reading above 7167? Thanks, Kind regards, Adrien
Hi Adrien, The developers have reproduced this and identified it as a bug in the current version of the Modbus library. It will be fixed it in the next version of this library (Modbus_TCP_10). ~ Martin.
Hello Martin,
Do you know if the error has been fixed in the meanwhile?
I can’t find anything about it in the release notes.
Thanks,Adrien
Sorry for the delay.
Yes, this was fixed in version 10 of the Modbus TCP library, but unfortunately this was not mentioned in the release notes.