Modbus tcp server support

Dear Sir/Madam
I want to use AXCF 2152 PLC work as Modbus TCP server.
in which, 2 client will connect at the same time to PLC.
Which library support this requirement.
Many thank.

https://www.plcnextstore.com/eu/app/1543

Here you go

Forum - PLCnext Community

PLCnext Technology from Phoenix Contact is a unique, open ecosystem for modern automation that is capable of meeting all the challenges of the IoT world.

Dear Sir.
It seems only client can connect.

Hello!
You can use several TCP server instances bound to the same listening port to manage multiple client connections.
BR