Monitoring Goose messages with IEC61850 app

Is it possible to monitor the incomming goose messages?

I wan’t to be able to act on the loss of a goose message on the bus e.g. put a cell in mode local if the goose message “mode remote” is no longer on the bus, or send an alarm…

Hello Wim

I forwarded your question to development.
There is no direct indicator, but there is a way to get it from the quality information.
Please have a look at the answer below:

There is no separate indication on the GOOSE subscriber side that directly signals a GOOSE communication loss to the application. The communication state can, however, be derived from the quality information of the data received through GOOSE.

On the subscriber side, the detection of missing GOOSE communication is based on the Time Allowed to Live (TAL) provided with the received GOOSE messages. If no subsequent GOOSE message is received within the applicable TAL, the corresponding data is considered outdated.
This is reflected in the quality of the affected data objects:

  • when using the Tc data types: Quality.Validity = Questionable and Quality-DetailInfo = OldData
  • when accessing the IEC 61850 q attribute directly: q = 0xC1

The same quality indication applies before the first valid GOOSE message has been received. The customer can evaluate this quality information in the PLCnext Engineer application and implement the appropriate reaction, for example switching the cell to local mode or triggering an alarm.

I hope this helps in achieving what you are trying to do.

BR
Mathieu