Hi, I’m working with the AXC 2152 through Ethernet/IP protocol, however the maximum information to be able to deliver is 256 bytes. Is there any way to increase the number of bytes written by the variables EIP_ IO_ OUTPUTS and EIP_IO INPUTS ?

Hi, I’m working with the AXC 2152 through Ethernet/IP protocol, however the maximum information to be able to deliver is 256 bytes. Is there any way to increase the number of bytes written by the variables EIP_ IO_ OUTPUTS and EIP_IO INPUTS ?

Hello Cris, the EIP_ IO_ OUTPUTS of 128 WORD’s and the EIP_IO INPUTS of 128 WORD’s can’t be expanded / edited. Could you give me a short information about your use case and which array size is needed in your application, please? Thanks & Best Regards Eduard