1.PNG2.PNG3.PNG4.PNG5.PNGHello everyone, I’m posting this message because I have to make a profibus communication between a Siemens „ET200S“ module and the „AXC F XT PB“ module. As explained on the phoenix website, I downloaded the „SYCON“ software, added the „gsd“ file of the ET200S and configured its profibus address in „AXC F XT PB“. I created the library by exporting it, but when I launch the program, the FAIL LED of the „AXC F XT PB“ module is red. I don’t know if there is a specific parameter to put in the „PLCnextEngineer“ software or in „SYCON“?
Thank you in advance for your answer
Here is the data sent by the AXC F XT PB module
In addition, I have the BF-D LED flashing on the AXC F 2152. In the documentation it says: „Link status present, no communication connection to the PROFINET controller“. However, I have a connector between my AXC F XT PB module and my AXC F 2152 PLC.
I understand that the problem was solved by replacing a faulty I/O card in the ET 200S station.