Proficloud TSD data buffering on AXC F 2152?

I understand that the IOT Gateway is able to buffer data locally when the connection to the Proficloud TSD service is interrupted. Is this Proficloud TSD data buffer feature also possible with the AXC F 2152? If not, are there plans to introduce such a feature?

Hi Martin, this feature is planned for end of this year. We will check wether it is possible to storage data while connection is interrupted. We will come back to you, when we know when the feature is available. Best Regards, Dennis

Hi, I have seen that now the AXC F 2152 has a TSD data buffer. For how long it can store data? Thanks in advance

Hello, The default configuration is to buffer data on the PLC for 10,000 seconds divided by the number of elements being logged. So when logging 1 element, data will be buffered for approximately two and three-quarter hours. 10 elements will be buffered for approximately 16 minutes, while 100 elements will be buffered for around 1.5 minutes. - Martin.