Ready|SystemError on AXC F 2152 with FW 2025.0.3

Hello,
when i try to upload my project to an AXC F 2152 controller the application does not start and i get the error “Ready|SystemError” in the WBM:

Screenshot 2025-11-14 102053.png

In my PLCnext Engineer project i am using the following libraries:

20251114_102216_NotificationsData.txt

Screenshot 2025-11-14 102119.png

What am I doing wrong?
See also log file attached.
I am using PLCnext Engineer 2025.0.3

Thank you!

BR
Josef

20251114_102216_NotificationsData.txt

Hello!
You have to update PLCnextBase library to 1.7.2 build 5
https://www.plcnextstore.com/world/app/1590
Also, it can be useful to provide type 1 system reset of plc after upgrade of this library.
BR

Hello Oleksandr,
thank you for your reply.
If i try to replace the PLCnextBase library with the 1.7.2 build 5 version i get the following error:

How can i resolve this?

Thank you very much!

BR
Josef

Unfortunately, can`t read text on screenshot

But it seems to me, that there is conflict with Solarworx library, which also try to bind PLCNextBase implementation
Try to remove Solarworx, then uptate PLCNextBase, then attach Solarworx again
BR

Hello,
Currently it is not possible to use the FW 2025.0.3 with the latest Solarworx. It is only possible to use the FW 2024.0.9 with the latest Solarworx or PCU 4.1.

BR
Marvin