Hi I have tried to test the HTML5_with_REST example from GitHub. I have uploaded the files and folders to the controller and also the project in PnE., The eHMI works fine but the HTML5 page is not showing any variables on the list or int the dropdown. User Authentification is also disabled.
Do i need to do anything else which is not described in the guide? ![Capture]()
Dear Dan, i need some more information from you to find the mistake.
* FW of the controller
* Please right-click on the website->Explore->Network-Tab
Which error messages will be displayed there?
* Which browser/version do you use?
* Did you change the ip-address in the [pxcapiclient.js](https://github.com/PLCnext/HTML5_with_REST/blob/master/Project/js/pxcapiclient.js "pxcapiclient.js") to the ip-address of you controller?
Best regards, Jonas
Hi Jonas The firmware is 2019.3 I am useing Firefox Quantum version 67.0.2 64-Bit (Newest version) In firefox i can not right-click on the website->Explore->Network-Tab In Chrome i have the same problem (See the screenshot) The IP adderess is not changed (See the screenshot)
![IP Address]()
I found a mistake in theHMIDemo.html - file. I fixed it and it will be updated in GitHub soon.
The updated is send to you by email. Replace this file and then the example should work.
If you have any questions do not hesitate to ask. Best regards, Jonas
Hello Kai, That last commit is this one: https://github.com/PLCnext/HTML5_with_REST/commit/57c0ba263ba1f862a0c71ef13e965acfb44ea264 … and I think it addresses the issue that Jonas mentioned above. ~ Martin.