I’m currently trying to do the following thing on the SFC add-on :
An emergency stop is activated, i set my SFC to HALT mode,
Then a button ‚Reset‘ is push, the SFC come back to step 1.
I found how to set to HALT mode, but i can’t find how to put the SFC to step 1.
How can i do ?
Here is the answer from the PLCnext Engineer support team:
if you set the variable to “Halt”-Mode you can operate via. the inputs
Step_ID and Activate_Step to the first step for example.
The right Step_ID can be select below the struct Step_States.
Important:
**The ID can be different to the Step count.**Example = Step 1 has ID 2?name=image.png?name=image.png?name=image.png
If you have additional questions do not hesitate to ask.
Hi Robin02,
first things first so check the help page for programming in SFC. You’ll find the FBs’ parameter description.
Then I would suggest something along this pseudo code:
IF ResetButton = TRUE AND SfcFB.Active_Operating_Mode = HALT THEN
//Go through all steps and deactivate them
WHILE(I < Step_States.StateCount) DO
SfcFb.Deactivate_Step(Step_States.StateList[I]);
I++
End_while
//Crawl through the structure and check the object property. Return the ObjectID of init step
InitStepID := FindInitStep(SfcFb.STRUCTURE);
SfcFb.Activate_Step(InitStepID)
End_If