Hello,
can someone please help me with may Question. I have the problem that i´m about to connect VISU+ with PLCnext and TIA. The Task is you push a Button in VISU+ and an Output in TIA gets activated. But how do i do that.

Wish you the best in life

basicly you could run this via the OPC_UA communication. The PLCNext controller is one OPC_UA endpoint in Visu+ and the Siemens controller the second endpoint.
To implement the OPC_UA function on the Siemens controller, please have a look at the Siemens support side. there you could find some examples for it.
In future please note the type of controller and TIA version. This would make it easier to point you in the right direction.
Peter Paul