VPN connection AXCF2152

Hi,
I am using mGuard secure cloud and Shrew Soft and i want to debug my PLC (2152) remotely via VPN. I already ping the PLC (192.100.0.175) and the mGuard (192.100.0.1) on Command Prompt and have response.
image.png

But I’m having some troubles trying to connect to the PLC on PLCNext Engineer (I’m using version 2022.9):
When I search the PLC on “Online Controllers” I set the option of connection on “Shrew Soft” but it doesn’t find any device. So, I cant even establish connection to start debugging or even writing the program on the PLC.
image.png
What i need to do?
Thanks!

I have not been successful using the Scan for Online Controllers…just like you.
Usually, you can go to the “Plant” view, right click on your controller, and select Connect. I use this routinely with PLCNext controllers via VPN.
PLCNE Online.jpg

The scan function uses the DCP protocol. It is based on MAC addresses and thus cannot be routed. That is the reason why you cannot scan for devices via a VPN connection.